I have an application with an I/O Integer tag from a SLC505 via DASABTCP. Periodically, when the application starts up, the tag's value goes to '0'. The tag has a non-zero initial value, I've cross-referenced the Intouch programs to make sure there's nothing writing to the tag on start-up.

The system is setup with a primary & failover node. The problem doesn't seem to be specific to either.

Any Ideas?

asked Nov 30 '09 at 17:13

Marc%20G.'s gravatar image

Marc G.
39017


I have seen this issue occur in a different setup; however, it might have the same cause. It might either be an issue with the Data Collection or Display Cashe. Two thing to check would be the Refresh of the Data Collection, and whether the Value is set to fail to a 'Zero' Value or Previous Value. The Second possibility would be the speed at which the HMI Display is set to refresh and whether you have the ability to Cache the information.

It can occasionally be associated with a Network BottleNeck where your HMI refreshes faster than your Data can be Displayed. These issues might not apply to your problem, but hopefully this helps.

link

answered Dec 08 '09 at 22:06

Luis%20R's gravatar image

Luis R
20816

Your answer
toggle preview

Follow this question

By Email:

Once you sign in you will be able to subscribe for any updates here

By RSS:

Answers

Answers and Comments

Markdown Basics

  • *italic* or __italic__
  • **bold** or __bold__
  • link:[text](http://url.com/ "title")
  • image?![alt text](/path/img.jpg "title")
  • numbered list: 1. Foo 2. Bar
  • to add a line break simply add two spaces to where you would like the new line to be.
  • basic HTML tags are also supported

Tags:

×5
×3
×1

Asked: Nov 30 '09 at 17:13

Seen: 458 times

Last updated: Dec 08 '09 at 22:06