I'm looking to monitor a pulse output from a plant's main gas flowmeter, and would rather not have to wire it back to a counter card on an unrelated PLC. The goal is to get flow logged in the plant's InSQL server, and the meter is close enough to a network connection, so I'm thinking about using and Ethernet I/O module like ADAM6000. Has anybody used something like this? Does anybody know if the WonderWare Archestra device integration toolkit contains something that will let me connect to this I/O.

asked Jul 27 '10 at 12:14

Marc%20G.'s gravatar image

Marc G.
39017


We did something similar using Moxa I/O modules connected using Modbus TCP/IP. The standard Modbus DAS from Wonderware worked great.

Luigi De Bernardini CEO Autoware S.r.l. unipers.

link

answered Jul 27 '10 at 12:51

Luigi%20De%20Bernardini's gravatar image

Luigi De Bernardini
261

You may use Point I/O from Rockwell Automation and configure a local counter (using DeviceLogix)

link

answered Jul 28 '10 at 20:00

Max%20Alp%C3%ADzar's gravatar image

Max Alpízar
1

I thought about this option first, but Point I/O is significantly more expensive. I can get these ADAM modules for under $200!

(Nov 09 '10 at 19:00) Marc G.
Your answer
toggle preview

Follow this question

By Email:

Once you sign in you will be able to subscribe for any updates here

By RSS:

Answers

Answers and Comments

Markdown Basics

  • *italic* or __italic__
  • **bold** or __bold__
  • link:[text](http://url.com/ "title")
  • image?![alt text](/path/img.jpg "title")
  • numbered list: 1. Foo 2. Bar
  • to add a line break simply add two spaces to where you would like the new line to be.
  • basic HTML tags are also supported

Tags:

×7
×1
×1

Asked: Jul 27 '10 at 12:14

Seen: 766 times

Last updated: Jul 28 '10 at 20:00