I have the following: - A CompactLogix controller with an ENBT card. - A SmartGuard600 Safety Controller on Ethernet/IP (1752-L24BBB) I followed the directions in the manual to setup a few bytes of "Ethernet/IP Target I/O" in the SmartGuard. I then configured the PLC through RSLogix5000 to add a Generic Ethernet Module ("ETHERNET_MODULE") with the following parameters:
This should work, but when I download to the processor, I get this error:
So I checked and the configured "input" size on the SmartGuard (direction of I/O is relative to the PLC) is 4 BYTEs. That should be equal to 2 INT's in the PLC. Not sure what I'm doing wrong. If anyone's done this before, please let me in on the secret. Thanks! |
|
I got it to work. I had to configure the SmartGuard600 with 2 Words of inputs and 2 Words of outputs even though I'm not using the outputs, or else it wouldn't communicate. Here's the configuration I used in RSNetWorx for DeviceNET to configure the SmartGuard600 Ethernet/IP I/O:
...and here's how I configured the CompactLogix in RSLogix5000 (same as in the manual):
Note that I still get a module mismatch (on the revision key) but I'm not sure how to fix that because it's a "generic" driver and there's nowhere I can set the revision numbers. |