Is there a way to monitor the status of an Ethernet I/O module (ENBT)? In particular, when communications is lost, to trigger a fault indication?
asked Jan 12 '10 at 20:45
Gabe 372●1●10
You can monitor the module entry status using a GSV command. When the I/O module is not responding, then the entry status is no longer equal to 16897.